English Support => General Support => Topic started by: gmonk63 on July 02, 2025, 07:15:25 PM

Title: Possible Bug
Post by: gmonk63 on July 02, 2025, 07:15:25 PM
We have a new temperature/humidity sensor  from WebRelay (X-410) which has been added to netxms to monitor temps. The weird thing is for each config poll a different address is seen and interface eth0 is changed to this external address which is not the address we assigned to the device and is external. The device has a single ethernet port and  still responds to the internal address we originally assigned. I have checked with another MIB browser with the IP and IF oids and I don't  see where this address is coming from. Is it possible netxms is generating these addresses ?  I am curious as to what the PING3 driver is and how it determined this device needed that driver.


Thanks
Title: Re: Possible Bug
Post by: Filipp Sudanov on July 08, 2025, 01:45:22 PM
PING3 is something niche and yes, looks that it's being auto-detected incorrectly. You can put PING3 into NetworkDeviceDrivers.BlackList server configuration parameter, this will prevent the auto-detection