I would like to collect the Environment Table from a Cisco Switch, but nothing happens. The table under last results displays only blank fields. For example i have configure the temperature sensor from a Cisco Catalyst 2960-S.
Could someone help me to configuring the snmp table correctly?
			
			
			
				You have to select .1.3.6.1.4.1.9.9.13.1.3.1.2 (or any other working OID inside .1.3.6.1.4.1.9.9.13.1.3.1) as table's base OID, and use .1.3.6.1.4.1.9.9.13.1.3.1.2, .1.3.6.1.4.1.9.9.13.1.3.1.3, etc. for column OIDs. I've created short document with working SNMP table example: http://wiki.netxms.org/wiki/Creating_SNMP_table_DCI (http://wiki.netxms.org/wiki/Creating_SNMP_table_DCI).
Best regards,
Victor