DCI Template with Threshold shows as a single alarm

Started by mdreher, October 27, 2017, 08:54:11 PM

Previous topic - Next topic

mdreher

Hey... having the strangest issue.

I created a template for the System.Uptime value from the netxms agent.  I created a threshold for this to create an alarm when this value went over 3456000 (40 days in seconds).  For testing I reduced the number to 864000.  The strange thing is, that instead of the alarm generating for each node, it generates a single alarm and increments the count... then just changes the source of the alarm a bunch of times.  Ideally I'd prefer if it generated a separate alarm for each node.  Am I doing something wrong here?

tomaskir

Your alarm key in the EPP rule that processes your event is wrong.

You need to make it per-node there.

mdreher