English Support => General Support => Topic started by: bulwer on January 27, 2014, 11:13:52 AM

Title: Node down alarm outside of polling time
Post by: bulwer on January 27, 2014, 11:13:52 AM
Got a very strange one here. We have 2 Kiosk PCs used at one of our sites to allow customers entrance to the centre. We want to monitor that these are staying up during the day so I added them both to NetXMS with just the standard Status DCI. I then set a custom schedule so it only collects the data when the PC should be on and stops overnight when they are manually switched off. According to the history of the DCI, this works perfectly. However, we are getting Node down alarms and therefore emails outside of the custom schedule for just one of these PCs when it is being switched off. The other PC should be switched off around the same time but we don't get an alarm for that which is what we want.

Probably one of those annoying problems you won't be able to replicate but I thought I would mention it on the off chance I have done something stupid. I have attached screenshots of the setup of the DCI in question but, as I say, the History shows that it is collecting data at the correct time - it is just triggering the alarm when it shouldn't be and doesn't appear to be collecting data.
Title: Re: Node down alarm outside of polling time
Post by: Dani@M3T on January 27, 2014, 01:31:50 PM
I see exactly the same issue with my custom schedule '* 8-24 * * *'
Title: Re: Node down alarm outside of polling time
Post by: Dani@M3T on January 27, 2014, 01:48:55 PM
For me the question is, what triggers the SYS_NODE_DOWN event. The default DCI 'status' has no threshold configured.
Title: Re: Node down alarm outside of polling time
Post by: Alex Kirhenshtein on January 27, 2014, 09:31:08 PM
It's generated internally, when server can't reach node via any allowed channel (ICMP, Agent, SNMP)

Easiest way is to have a rule in a event processing policy which silently ignores SYS_NODE_DOWN during off-hours.
Check attached screenshot for sample configuration.

Please note that this EPP is processed from top to bottom and by default all rules are processed (unlike "first-match-win" in thresholds), so this rule should be above any other SYS_NODE_DOWN related rules.

Description of "TIME" structure (returned by localtime()): http://wiki.netxms.org/wiki/NXSL:TIME

Update: script should be like "if (now->hour >= 20 || now->hour <= 8) ..."

Quote from: Dani@M3T on January 27, 2014, 01:48:55 PM
For me the question is, what triggers the SYS_NODE_DOWN event. The default DCI 'status' has no threshold configured.
Title: Re: Node down alarm outside of polling time
Post by: Victor Kirhenshtein on January 28, 2014, 09:59:16 AM
Actually, there is an etrror in the script: you should use || (logical or) instead of && (logical and).

Best regards,
Victor
Title: Re: Node down alarm outside of polling time
Post by: Dani@M3T on February 07, 2014, 05:56:18 PM
thanks for this 'workaround'. But in my opinion this is not very elegant, it's inconsistent. All DCIs of a node are managed by there own 'custom schedule', only for 'status' we need an event processing policy. A 'custom schedule' for the status of a node would be a good feature. Or maybe SYS_NODE_DOWN event could be triggered by the 'status' DCI, so the 'custom schedule' of this DCI could be used.
Title: Re: Node down alarm outside of polling time
Post by: Victor Kirhenshtein on February 11, 2014, 02:02:00 AM
It is possible to add threshold to status DCI and generate some custom event instead of SYS_NODE_DOWN, and do all processing for this custom event. But status and SYS_NODE_DOWN have one important difference - status also takes current alarms into consideration. So, if there is active critical alarm, status will be 4 (critical), but SYS_NODE_DOWN will not be generated, because node itself is reachable. Starting from upcoming 1.2.12 release, it is also possible to create DCI which will check node down flag. If you put threshold on such DCI and will generate some custom node down event, you'll get exactly what you need. To create such DCI, create new DCI with source "Internal" and parameter name "Dummy", and use the following transformation script:


return ($node->runtimeFlags & 0x04) ? 1 : 0;


This DCI will return 1 if node is down and 0 otherwise.

Best regards,
Victor
Title: Re: Node down alarm outside of polling time
Post by: jdowney on March 08, 2017, 05:39:43 PM
Hi looking at doing the same we have some nodes which are either rebooted nightly or weekly. Is there a way to implement per node of no status updates during this time?

Thanks
Title: Re: Node down alarm outside of polling time
Post by: jdowney on March 13, 2017, 01:07:29 PM
would it be an option to create a maintenance schedule for this?

I've tried to use Cron Maker to set a cron schedule within the task but it does not seem run. Any ideas on what I'm doing wrong or if there is a better way to do this. 

www.cronmaker.com -
Quote0 30 23 ? * MON,TUE,WED,THU,FRI *
(Every weekday - Monday - Friday 23:30)

Thanks
Title: Re: Node down alarm outside of polling time
Post by: jdowney on April 03, 2017, 06:38:21 PM
Nudge, Nudge Anyone know what I'm doing wrong or is there an issue with 2.1-M2 which is why this is not working?
Title: Re: Node down alarm outside of polling time
Post by: Victor Kirhenshtein on April 03, 2017, 08:04:16 PM
Hi,

as far as I can tell your schedule is not valid cron expression. As stated on web site "Generated expressions are based on Quartz cron format". NetXMS supports subset of UNIX cron format (see here for example: https://en.wikipedia.org/wiki/Cron#Modern_versions (https://en.wikipedia.org/wiki/Cron#Modern_versions)). It only supports *, /, -, L, and lists. Try to change your schedule to


30 23 * * 1-5


Best regards,
Victor
Title: Re: Node down alarm outside of polling time
Post by: jdowney on April 04, 2017, 11:50:20 AM
Thanks a lot this has resolved our issue with overnight daily reboots.
:)
John